Hi I have fitted out several set ups similar to yours & have found that putting more than 3 per circuit causes problems.
These fittings are very inductive so have very high inrush currents at switch on, this can cause switches to burn out and even C curve MCB's to trip.
Now I wire them in pairs on 3 circuits via a 3 pole contactor, then you can use a single weatherproof switch to control all 6 fittings.
This keeps wiring runs short as don't have to loop down to switches, I fit contactor next to dist bd take Neutrals straight to each pair of lights, lives/lines via contacts and control circuit from board to switch and back to contactor coil, normally get away with C10 mcb's, wire in 2.5mm2 if long runs,
regards SPARX