Post
by sparx »
Mon Aug 04, 2008 10:17 pm
Hi Martin,
Ericmark the flatterer knew this would draw me out....he is being undully modest!
I am not entirely sure which way to answer this, as Eric says there are differences under latest regs from older ones.
If you have an existing installation and just want to improve it then as he says make sure you test the rod alone, not connected to other bonding, this will give the worst case reading which will always come down when bonding reconnected, due to parallel paths. Thus rod reading must be low enough to trip RCD. It was normal to have 100mA rcd on main but not good enough for sockets so led to split load boards, rcbo's etc for some circuits. In theory a 30mA rcd could have a rod resistance of up to 1666.6ohms using 240v or a 100mA trip could have a resistance of up to 500 ohms however guidance note says over 200 ohms"may not be stable".
From your readings it would seem you have a reasonably good earth reading of 15 ohms but as Zs is only 0.66 higher I presume bonding was in place when doing Ze, check it again minus bonding to be sure.
I would not want to leave whole house on 100mA trip so without expense, time etc of changing board I would change RCD to 30mA one, not up to latest standard but much safer than now.
Went to house today where C#rry's had deliver a new cooker but would not connect it as "loop reading too high" @ 70 ohms "should be less than 0.8 ohms missus, you got a problem!" T.T. system! they didn't even look.
came from town where all TN systems.
Is TNC-S (pme) not available in your area? that would give a slightly more reliable earth path.
welcome to forum BTW,
regards SPARX