by htg engineer »
Mon May 19, 2008 9:12 pm
15mm or 10mm will work and will both last as long as each other - if looked after.
As for 15mm distributing the water/heat better, it doesn't affect it if designed and installed properly. You could use 15mm,10mm,8mm,6mm or drinking straws, as long as you don't mix and match the sizes the water will be evenly distributed.
If a system is badly designed that is when the distribution will be affected, mixing 15mm and 10mm will affect perforamnce and distribution. Pick a size and stick to it it's either all 15mm or all 10mm.
People tend to be put off by 10mm because of blockages, yes in older systems that weren't flushed, no inhibitors added, connecting a new boiler to old pipework etc. A new pressurised installation with 10mm pipe will last as long as a new installation with 15mm pipe, if it is looked after - adding inhibitors and replacing when the system is drained.
htg