by ericmark »
Thu Sep 25, 2008 1:28 am
If the low Zs reading is due to any parallel paths then the reading is correct. But looking at reading given seems unlikely.
Many people when checking the Ze reading do so with main switch on and everything running. Really, the reading should be made with everything off and all earths disconnected from main incoming earth.
Although we assume an Earth Loop Impedance of 0.35 ohms on a TN-C-S supply it could once the water pipes and gas pipes etc are connected be well below that figure.
So to start with would you say that 22 meters of cable seems around the right figure for what you know. Remember if will allow for a +/- error of 0.1 then between 19 and 24.5 meters how does that match up?
Looking at 0.5 reading and comparing with 0.8 the Ze reading would be need to be very low and a really good parallel path also. As a result one starts to look at the meter.
Normally one selects a socket at work and one writes on it the measured Earth Loop Impedance each time one takes the meter out you first retest that socket. Should something go wrong with the meter it then gives one a good indication that it has gone out. Once inspection and testing becomes a regular job you soon get to know what to expect. This is exactly what happened with your boss he looked and realised something was wrong.
You post is unclear to me. If your saying because it is not RCD protected you have removed the bathroom bonding then this will not explain the reading.
If you are saying the bathroom is bonded and should you remove it. Then yes for test but no on permanent basis and in real terms I would not remove but just note that it was in place on the paperwork.
Also all circuits in bathroom would need to be RCD protected to be able to remove earth cross bonding not just the circuit you are working on.
Do remember this is only an excise as you may use inquiry, measurement, and calculation to get results and you do not need to duplicate so once you have measured R1 + R2 there is no need to then use the earth loop impedance tester as well. It is a good idea but not required.
I will guess your boss just wants you to realise why you got the reading and once you tell him you think because of parallel earths you got the reading then he will accept it he has done what he wanted and made you think.
Eric