by ericmark »
Mon Sep 08, 2008 11:20 am
Thank you jaffa19 I had missed mephistico comments
“Bear in mind also that the bonding may be undersized to current regs & a test/inspection is probably due.”
This is true and often there is no earth connection where original bonding was in bare copper and very small and has been broken long ago and I have seen electricians fail to remove bonding to water pipes etc. before testing so giving completely wrong results this is dealt with in the IET/IEE wiring maters summer 08 issue 27 available for down load off web site.
”With an older installation there is no need to comply with 17th edition regulations. You should concentrate on getting it up to 16th edition (split load board, sockets on RCD 10mm main bonds, supplementary earthing etc)”
Once anything is updated, then that must comply with 17th if designed after 31st June. It is causing major problems where minor works are completed and they need RCD protection at the origin due to buried wires. As to split load boards either double or triple one can’t just fit and assume it will comply.
“314.2 Separate circuits shall be provided for parts of the installation which need to be separately controlled, in such a way that those circuits are not affected by the failure of other circuits, and due account shall be taken of the consequences of the operation of any single protective device.”
So if combining the down stairs sockets and up stairs lights on the same RCD or visa versa when a fault occurs on a socket and one can’t see ones way to the consumer unit it would contravene the regulations but if there were wall lights running off socket supply so there would still be light to see ones way to consumer unit it would not the same applies if emergency lights are used. 314-01-01 and “314-01-02 A separate circuit shall be provided for each part of the installation which needs to be separately controlled for compliance with the Regulations or otherwise to prevent danger, so that such circuits remain energised in the event of failure of any other circuit of the installation, and due account shall be taken of the consequences of the operation of any single protective device.” of the old 16th Edition regulations were very similar in their wording and one does need to consider if the regulation was ever any different or have we been interpreting wrong over the last 16 years?