by sparx »
Tue Oct 21, 2008 8:41 pm
Hi,
Not to detract in any way from Ericmarks excellent maths I can say that I have run my arc welder from my house supply to my workshop for the last 35 years without many problems.
It is rated for 130A continuous/160A short time.
For most jobs I have rarely needed to go much over 90A & only occasionally blown the 13A plug fuse.
I then installed a 16A blue industrial socket as used for caravans/generators etc. and the matching plug on welder.
The supply to workshop comes via a 2.5mm2 Pyro fed from a 30A type 2 MCB in my house consumer unit which has a 30mA rcd main switch which I have tripped on odd occasions when striking-up.
Only complaint from 'senior Management' is the lights flicker sometimes!
As Ericmark says the maths don't add up as conditions change during use,
eg 110A X 48V = 5,280 va / 230V = 22.96A on strike, but as soon as arc struck gives shorted output so secondary volts drop off rapidly to maybe as low as 24V , then 110A X 24v = 2640va / 230V = 11.5A!
So forgetting my dodgy maths(please), ask yourself do you really need to weld that thickness of metal?
I can weld heavy angle iron brackets etc. with less & what about a Mig/Tig ?
regards SPARX