boiler ideal mexico 2 honeywell

by kevcrabtree » Tue May 08, 2007 9:05 pm

wont ignite had problem before need to know start up sequence please

Paul Pepper
Tradesman
Tradesman
Posts: 38
Joined: Fri May 11, 2007 7:02 pm

by Paul Pepper » Sun May 13, 2007 5:42 pm

Which model - there's a lot of different types - GC no off data badge would help!

kevcrabtree
Labourer
Labourer
Posts: 2
Joined: Tue May 08, 2007 8:58 pm

boiler wont ignite

by kevcrabtree » Sun May 13, 2007 6:42 pm

thanks paul the the number is 41-429-49. any help appreciated

Paul Pepper
Tradesman
Tradesman
Posts: 38
Joined: Fri May 11, 2007 7:02 pm

by Paul Pepper » Tue May 15, 2007 7:06 pm

Sorry to be so long replying1

Assuming pilot is lit and there is 240v live into the boiler from system controls, check for 240v live on gas valve terminals. If no power present - boiler thermostat is prob at fault. If live present, gas valve prob duff.

Hope this helps!

Paul