I have currently got a floor standing cast iron boiler (Myson Marathon 1000B) that I wish to upgrade to a more efficient condensing type. ( I was looking at the Glow worm flexicom range). The current system is gravity DHW and pumped CH.
There are 4 pipes coming down to the boiler. 2x28mm flow & return for the DHW and 2x22mm flow & return for the CH. The 28mm pipes go up to the attic where the indirect DHW cylinder is located. The 28mm flow carries on past the cylinder up to the F&E tank. The cold water makeup from the F&E joins into the 28mm flow adjacent to the DHW cylinder.
I wish to convert this to a fully pumped ‘S’ plan system. In order to maintain an unrestricted path from the boiler to the F&E vent means I would need to place the 2 port motorised valve in the return 28mm pipe from the DHW cylinder. Similarly it would mean placing the circulating pump in the return leg before the boiler. Commoning up the CH & DHW flow pipes at the boiler outlet.
All the diagrams I have seen show the pump and the motorised valves in the flow side, after the boiler. Is there a problem in putting the valves and pump in the return side before the boiler? After all, the pump is just there to circulate the water around the system. The static pressure comes from the height of the F&E tank? So it shouldn’t overflow the vent into the F&E? Or am I missing a trick here?
I realise that I will need a bypass circuit for pump ‘run on’ when both valves are shut but I can accommodate that.
I would have thought this would be a common upgrade / problem but can’t find any references in the forums. Any hints / tips would be much appreciated.
Thanks
Matt