Eric/ Forum,
Sorry to be a pain
Just want to check this with you please before actioning :
[u]Question on fitting the external gland[/u]
With regards to fitting the 6mm SWA cable to outside MK Plastic weatherproof socket using the SWA gland it comes with a nut and earth tag.
From what I am reading you should put a bolt through the mounting socket box (even though its plastic) through the eye of the earth tag to earth it
However if I do this it will affect the IP rating for the weather proofing of the box.
Should I be using a Piranha Earth Locking Nut instead i.e :
http://www.tlc-direct.co.uk/Images/Prod ... RPEN20.JPG
I can then use and earth wire with and eye to connect the earth to the Piranha nut.
In fact rather than messing about with bolts and having to drill through the box whether it be metal clad or plastic could I not use Piranha nut instead of the nut and earth tag even if I am glanding to a straight forward metal 2 x 2 box?
Apart from being a bit more costly are their any issues with this?
regards
J. A.P