by ericmark »
Wed Nov 19, 2008 5:44 am
First be aware consumer unit changes come under Part P that said I’ll try to answer questions.
To extend sockets all new sockets under 20 amp i.e. all 13 amp sockets need RCD protection except where they supply a designated piece of equipment like an oven or freezer. You could fit all RCD sockets to comply with this. However also all cable buried in walls, ceilings under floors etc at less than 50mm also needs protection this can be by using a RCD or by using one of the special cables etc. So if all extension wiring is in Al-tube cable and RCD sockets are used it would comply.
Lighting with the exception of the bathroom does not need RCD protection however as with sockets the cable may again using Al-tube cable to BS 8436 would comply there seems to be four major manufactures of Al-tube cable GuardianTM, EarthshieldTM, FlexishieldTM, AfumexTM assuming no outside, kitchen, or bathroom work is required then this may be best option to avoid Part P.
As to replacing the consumer unit if all RCBO’s are used there is no problem but where one wants to use just Twin RCD’s you need to consider the risks and results if one RCD should trip.
Regulation 314 does not say you have to fit two RCD’s but refers to dividing into circuits to avoid hazards and inconvenience with special note on danger that may arise from failure of a single circuit such as a lighting circuit. This has been the case for many years but it now includes reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor currents produced. This points out that the dividing into circuits also includes RCD as well as MCB and maybe we should have been considering twin RCD’s for many years? But the way it is worded using emergency lighting would alter what is required. As would battery backed smoke alarms etc.
Hagar do an example of wiring a twin RCD consumer unit where upstairs lights are combined with downstairs sockets and downstairs lights with upstairs sockets and most people seem to think this complies.
However one may consider having any sockets combined with lights is wrong or one could consider in small houses what is used is no different to a caravan which has to supply all power through two RCD,s in series rather than is parallel?
Here we need to consider who is signing the paperwork and if the LABC say you need to use Two RCD’s plus a RCBO for smoke alarm that’s what you need. And I would suggest you check with who ever is signing paperwork as to how they want it configured.
As to common problems well most are to do with RCD’s and I will try to list a few.
1) Cooker or other heating elements which may be hydroscopic having absorbed water causing the RCD to trip.
2) Stairs lighting having been wired with only twin core strappers on two way lighting causing borrowed neutrals scenario if lights switch on with one combination of switches RCD trips but may work OK with another combination.
3) Damp and dust causing leakage and so RCD to trip.
4) Combination of numerous leakage paths including computer surge protection building up and causing RCD to trip.
Except for No 2 the more RCD devices the less likely it is they will trip.
RCD’s should not trip at half their rating so with 8 RCBO’s you could have 8 x 15ma or 120ma leakage without it tripping assuming all circuits with same leakage but with twin RCD’s only 2 x 15ma or 30ma before you get problems. Also of course where one can’t cure fault for example faulty cooker one could replace the RCBO with a MCB as a temporary measure until the cooker is changed or repaired but one could not really justify removing the protection for whole house as a temporary measure.
It is normal to do a full PIR before starting on a consumer unit change as very hard once started to convince a customer why it costs more. The main problem is lights the Electrical Safety Council to which most the regularly bodies subscribe say if there are no earths to lights certain measures must be taken and if not then the electrician must refuse the work. A little late if he has already started hence always full PIR before starting then another once complete. It is of course all this inspection and testing which raises the price of the job and one is sometimes temped when everything looks good to cut corners and only test on completion.
Does that answer your questions?
Eric