http://www2.theiet.org/Publish/WireRegs ... itions.pdf is out dated but does show zones. Or
http://www2.theiet.org/Publish/WireRegs ... _walls.pdf A cable installed under a floor or above a ceiling shall be run in such a position that it is not liable to be damaged by contact with the floor or the ceiling or their fixings. A cable passing through a joist within a floor or ceiling construction or through a ceiling support (e.g. under floorboards), shall: (ii) incorporate an earthed metallic covering which complies with the requirements of these Regulations for a protective conductor of the circuit concerned. the cable complying with BS 5467, BS 6346. BS 6724, BS 7846, BS EN 60702-1 or BS 8436, or be installed in a zone within 150 mm from the top of the wall or partition or within 150 mm of an angle formed by two adjoining walls or partitions. Where the cable is connected to a point, accessory or switchgear on any surface of the wall or partition, the cable may be installed in a zone either horizontally or vertically, to the point, accessory or switchgear. Where the location of the accessory, point or switchgear can be determined from the reverse side, a zone formed on one side of a wall of 100 mm thickness or less or partition of 100 mm thickness or less extends to the reverse side.
Far easier to use BS 8436 Ali-Tube cable i.e. GuardianTM, EarthshieldTM, FlexishieldTM, or AfumexTM no need for capping then.
As to heights only valid on new build and is Part M not wiring regulation there is a Link in Projects to Part P from that you will find Part M
Eric