by ericmark »
Thu Dec 11, 2008 6:06 pm
Except where extra low voltage lighting was fitted from new light switches rarely have a neutral connection.
To fit outside lights as an add on normally one would connect to the power circuit.
Because 5 amp is normally the max one can supply to lights when supplying from a socket normally we use either a switched fuse connection unit (FCU) or a grid switch the latter will allow fitting a fuse unit as one of it’s options.
Also since socket supplies are normally already RCD protected one does not have to use Ali-tube cable or install an RCD. But when taking a supply from a lighting circuit because of the change in regulations often it will also involve either use of Ali-tube cable or fitting a RCD to protect the new installation which is not so easy when taking the supply from a ceiling rose.
Even if the existing sockets are not RCD protected it is relatively easy to install a RCD fused connection unit at the origin of the additional circuitry.
As to wiring in series as I think you are talking about I would consider this as dangerous and would advise against it although not against BS7671
I will also point out Parts P and L1 the latter requires outside lights should not exceed 150 watt and must auto switch off when not required or be of a type that only lamps at 40 lumens per watt or better can be used. And except when there is no external junction boxes etc etc it can also come under Part P.
I would agree in most cases you would likely not get caught but if the outside lamp was to upset a neighbours then it may cause problems or if you try to sell the house.
Eric