a radiator problem that is driving me mad!!!
Help and information on all topics relating to your central heating, air conditioning and ventilation issues.

5 posts   •   Page 1 of 1
Rob Gibson
Apprentice
Apprentice
Posts: 5
Joined: Thu Nov 27, 2008 6:52 pm

a radiator problem that is driving me mad!!!

by Rob Gibson » Wed Dec 10, 2008 9:41 pm

Are you sitting comfortably? Then I'll begin - this is a real saga!!!

I live in a terraced house and have a very old CH system which generally works quite well. However there is one problem - one radiator never works and is always cold. All the rest get hot immediately. I actually replaced it with a new radiator and newly fitted TRV to se if that would solve the problem but it didn't. The old radiator had always been cold but I was told that it had worked well at one time.

The pipe under the lockshield gets very hot when the heating is on. I have tried bleeding the radiator until water comes out. I have tried turning all the other radiators off and then put the CH on to see if this one radiator would work but to no avail.

I have tried tapping the TRV and remving it to ht the pin which moves and is new anyway so should be okay!

I have tried turning the lockshield off and putting the TRV on full and then bleeding the water out based on advice received from a plumber. Whilst doing this the pipe under the TRV got hot and for a very short time the top of the radiator got very faintly hot but the bottom remained stone cold. After emptying seven basins of water I gave up trying to drain it further.

I am really at the end of my tether now with this as it is obviously winter, my living room is cold and I have paid for a radiator that doesn't work!

Please can anyone help me. Is it a balancing problem?

Thanks

Rob

Steve the gas
Site Agent
Site Agent
Posts: 780
Joined: Sun May 04, 2008 8:07 am

by Steve the gas » Thu Dec 11, 2008 5:34 am

Hi Rob,

Yes balancing may help, but, I would swap the valves around.
The TRV you have MAY be a one way type (most new ones are 2 way)
Also throttle those rads down that get hottest quickest etc.

Hth

plumbbob
Project Manager
Project Manager
Posts: 1892
Joined: Wed May 07, 2008 10:59 pm

by plumbbob » Thu Dec 11, 2008 4:33 pm

Sounds as if the pipework to the radiator is partially blocked. This could be with sludge or even an airlock. To find out and clear it, turn off the valves and disconnect them from the rad. If the pipes don't move you need to remove the rad. Using a short length of flexible hose, connect one end to one of the valves and place the other end in a bucket. Open the rad valve fairly wide. Run until the water runs clear or air is expelled. Repeat for other valve.

nitro23456
Foreman
Foreman
Posts: 346
Joined: Sun Aug 12, 2007 7:19 pm

by nitro23456 » Thu Dec 11, 2008 7:06 pm

you never actually mentioned opening the lockshield further, only closing it.

cueball
Apprentice
Apprentice
Posts: 9
Joined: Tue Apr 24, 2007 10:20 pm

by cueball » Fri Dec 12, 2008 2:39 pm

Hi Rob,
I came across this exact same problem last week, and here's what sorted it for me:
shut both valves, take rad off, open both valves in turn to find which side is blocked, trace this pipe back to joint that tees off to another radiator ( I had to remove some skirting board and boxing in). Drain system and de-solder this joint.
If problem is same then this joint will be blocked, hence, replace.
Good luck.