by sparx »
Mon Jan 26, 2009 10:23 pm
Hi again, it may be as KUZZ suggests starting current, unfortunately with RCBO's there is no easy way of knowing if tripped by earth leakage or overcurrent, one reason I don't care for them.
It is usual for most RCBO's to be type C however yours may be type B, if so it may be possible if circuit length/impedance allows to have it changed , still 32A but greater inrush current.
The leckie who changed the board must have given you a set of test sheets on which you will find a reading of Zs for the circuit which will tell if chane possible,
regards Sparx