by sparx »
Wed Mar 04, 2009 8:37 pm
Hi Dadwood et al,
just to give an easy eg.
if say you have a ring circuit and a lighting circuit plus a cooker on a consumer unit with a main 30mA rcd as main switch, plus a local 30mA rcd socket or spur on the ring.
the rcd socket / spur will see just the leakage from the downstream device (washing mc. say) but the main one will also see leakage from washing mc. plus all other circuits, so in practice the upstream device will always trip first, sometimes without the local one tripping at all.
EG, lights leakage 5mA, cooker 10mA, so already approaching main rcd's limit (which dispite its 30mA rating usually trip around 19-27mA), therefore washing mc leakage of say 10mA takes main rcd over limit (5+10+10 = 25mA) but local rcd only sees 10mA.
regards SPARX