Dimmer Switch
Ask questions and find answers to many subjects relating to electrics and electrical work

3 posts   •   Page 1 of 1
venom78
Labourer
Labourer
Posts: 4
Joined: Sun Jan 25, 2009 12:25 pm

Dimmer Switch

by venom78 » Mon Mar 09, 2009 10:39 am

Hi all

A fuse in my fuse box went off the other day. One of my downlights was causing the problem. At closer inspection, I found that the connecter (plastic) connecting the mains to the transformer had melted. Also, the transofrmer had blown.

I replaced the connecter as well as the transformer and switched on the lights. The lights went on and everything looked fine but I realised that the dimmer switch did not dim the lights anymore. They simply went on and off. Did the surge blow the dimmer? Do I need to place the dimmer? and if so what is the wattage that I need. Below is what I currently have:

4 downlights. Each 50W 12V
4 dais DA-E60 Dimmable Transformers (12volt TRANSFORMER FOR DOWN LIGHTS 60w/VA)
1 Dimmer switch

Thx

jaffa19
Apprentice
Apprentice
Posts: 16
Joined: Sun Sep 07, 2008 10:01 pm

by jaffa19 » Sun Mar 22, 2009 10:25 pm

Hi Venom

yes change it, a 400w dimmer will do the trick. as you've halogen lamps the user instructions show you to use a higher rated dimmer due to the current draw thru the circuit. A lower rated dimmer will naff up real quick

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Sun Mar 22, 2009 10:39 pm

Hi most likely dimmer U/S, 4X50 = 200va, nearest size is 240va/watt dimmer, check suitable for dimming transformer lnductive loads, not all are,
regards SPARX

3 posts   •   Page 1 of 1
It is currently Fri Nov 22, 2024 9:38 pm