Second Consumer Unit located distant from Service Inlet
Ask questions and find answers to many subjects relating to electrics and electrical work

2 posts   •   Page 1 of 1
skol
Labourer
Labourer
Posts: 1
Joined: Sat Mar 14, 2009 5:28 pm

Second Consumer Unit located distant from Service Inlet

by skol » Sat Mar 14, 2009 7:05 pm

What is the protection requirements for providing a second CU 4.7m distant from the main service inlet which consists of a 60A sealed-fuse, meter and 63A house RCBO (or it might be just an RCD, I can't tell)?

Must I have a near fused DP switch to protect the cable traversing from the service inlet 4.7m to the distant CU? The distant CU has its own switch anyway (just like the near CU).

Any ideas?

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Sat Mar 14, 2009 8:23 pm

Hi Skol,
It depends how its to be connected to incoming supply, eg if going from a spare way on original bd, eg from a 50A mcb as a sub main then no other isolation required.
However if using 'Henley blocks' to split 'tails' then to comply there would have to be a local isolator, as i'm sure the 'part P ' registered leckie doing the job will be happy to confirm,
regards SPARX