Just to add further confuson, bless the penpushers and regulators, if your house is wired to the 17th with a shedload of RCDs in your consumer unit supplementary bonding is no longer required in a bathroom. Pre 17th wiring it is required.
However if the circuits in the bathroom are RCD protected (as they will be if a new fan, lights etc have been fitted in a recent upgrade under the 17th) and the rest of the house is to the 16th supplementary bonding is still NOT required although there is no reason not to do it if you so wish.
Just for completeness there has been no need to provide supplementary for metal kitchen sinks and sink pipes since the 15th.
Edited for correction.