by rosebery »
Thu Mar 26, 2009 9:46 pm
What is the reading on your pressure guage? If its too high and the filling system isn't isolated then the PRV will operate and you'll get your leak!
If its dropping then the PRV isn't seating properly and the filler mechanism will be shut off.
If its in the correct area constantly then you could be looking at a situation where the PRV is letting by but the fill mechnism is topping it up at the same rate.
So theres lots to check before getting involved in changing/fixing a PRV that may not need to be fixed!
"When in use" from the original post implies that it only drips when the boiler is fired up. That says to me a further possibility. The pressure is too high in the system when it is cold (2+ bar) so when the water is heated the pressure will rise to above 3 bar and the PRV (set to 3 bar) will open.
Let some water out so that the pressure is 1 - 1½ bar when cold and see what happens when the system fires up.
As you say you can't find a filling loop then I suggest you have the built in link. Its accessible by droppingthe front panel and pulling out the "tray" that sits under the boiler (if said tray is actually there!!) Make sure the valve is shut and the key removed.