by cdk7474 » Sat Apr 25, 2009 6:13 pm

This afternoon the radiators started getting hot even though the thermostat was turned right down, I switched the switch on the front of the boiler (Potterton performa 24) to water only and the boiler was still fired up. I also switched the timer control to the off position and it was still alight, so now ive turned it off completely, Any suggestions or reasons for this would be much appreciated thanks.

Steve the gas
Site Agent
Site Agent
Posts: 780
Joined: Sun May 04, 2008 8:07 am

by Steve the gas » Sun Apr 26, 2009 7:23 am

This suggests that the diverter valve is passing hot water into the heating circuit.

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Sun Apr 26, 2009 9:58 am

Check sensors/frost stat.


htg

cdk7474
Apprentice
Apprentice
Posts: 6
Joined: Sat Nov 29, 2008 2:32 pm

by cdk7474 » Mon Apr 27, 2009 5:41 pm

thanks peeps for the information/advice, will take a look and get back to, thanks again

arnauda
Labourer
Labourer
Posts: 2
Joined: Fri Apr 24, 2009 6:56 pm

diverter valve

by arnauda » Mon Apr 27, 2009 5:48 pm

I have a similar problem. The central heating is switched off but when the hot water timer comes on , the radiators are getting hot.

If it is the diverter valve, how costly is it to have this repaired by an engineer?

Steve the gas
Site Agent
Site Agent
Posts: 780
Joined: Sun May 04, 2008 8:07 am

by Steve the gas » Tue Apr 28, 2009 5:42 am

Depends on the RGI but I would say about £80 + parts

bd3cc
Foreman
Foreman
Posts: 323
Joined: Wed Jan 30, 2008 8:02 pm

by bd3cc » Thu Apr 30, 2009 12:40 am

It does sound like the diverter valve.
these can be replaced easily, as it is the actuator or head which is at fault, and the just screw on/off. Any one can do it,=. Just note the model number, go to a plumbers merchants get the actuator, and refit. take a note of the electrical conections, make sure to turn off at mains and refti/ recoonect exactly as was.

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Thu Apr 30, 2009 7:21 pm

bd3cc - isn't the Potterton Performa 24 a combi boiler ?

Therefore it will have a diverter valve ?? not a three port valve as you're describing - big difference and not easy to change if you're not sure what you're doing!!!


htg

rosebery
Project Manager
Project Manager
Posts: 2021
Joined: Wed Sep 26, 2007 9:55 pm

by rosebery » Fri May 01, 2009 12:30 am

Surely a three port valve can reasonably be described as a diverter valve?

Cheers








(puts wooden spoon back in drawer!!)

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Fri May 01, 2009 4:35 pm

If you actually read the post I am not saying a three port valve cannot be described as a diverter - the point I was making is that it's a combi - he is saying to change the actuator head/motorised valve - if it's a combi it might not have one, if it does - it might not need re-wiring.

If people want the correct advice they need to give the correct info - as a TRADESMAN I am explaining that there is a between a three port diverter valve and a diverter valve, the motorised head or actuator cannot be changed as described.

It can be described as a three port diverter valve, or a two port diverter valve. But 'diverter valve' alone would normally be taken as referring to a combi boiler

I have asked before and you either refused to reply or didn't see my post, I asked if you were in the trade or had any trade behind you ? without the reply I have to assume not. I am - the advice I offer is correct.

If it's a hydraulic diverter valve, where's the actuator/motorised valve ? how would I change it ?



htg

rosebery
Project Manager
Project Manager
Posts: 2021
Joined: Wed Sep 26, 2007 9:55 pm

by rosebery » Sat May 02, 2009 11:41 pm

I was pulling your leg!!!!!!!!!!
wasn't it obvious??
obviously not!

Cheers

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Sun May 03, 2009 10:13 am

Sorry - missed the - (puts wooden spoon back in drawer!!) part of your post.

I assume that was to indicate you were 'pulling my leg'. Although haven't a clue what it means, must be a regional thing ? or an age thing as i'm only 25.

Or is that the clue to your trade ? baker or chef ? lol

Thanx
htg

rosebery
Project Manager
Project Manager
Posts: 2021
Joined: Wed Sep 26, 2007 9:55 pm

by rosebery » Sun May 03, 2009 11:25 am

Wooden spoons are for stirring!

Hadn't thought of it as a regional thing - thought it was universal.

Age thing nah! Age and cunning will overcome youth and enthusiasm any day.