by timeemit »
Tue Jun 02, 2009 12:52 pm
[quote="kbrownie"]timeemit,
Is there a hob above the cooker, if so how high is the original point? as this could be an issue regarding heat.
You can't put a terminal block in back box to make a joint, then blank it and plaster over that as all joints like this should be left so you know a live cable is routed through that area and all joints like this should be made easily accessible too. In case of faults so can be inspected.
KB[/quote]
Thanks..KB
1.The original switched dbl pole cooker point will be 330mm directly above the hob. I would like to move it slightly to the right so not as to be directly over hob, to a sgl pole cooker switch.
2. Thinking now to see if there is enough slack in ceiling void to pull extra cable down to new point. If not maybe connection in original backbox with a metal blankplate exposed above hob, messing up the whole splash back idea, MISSES WILL BE HAPPY....NOT.lol
Another thing am i right in saying that if my hob is 5.8kw and oven is 2.5kw = 8.3kw its ok to go with existing 6mm cable, 45A single pole cooker switch with a 40A CU fuse.