What size cable do I need when installing the primary earth to the stop tap and gas meter to the meter box?

This may have been covered before for that I apologise.

Many Thanks M

BLAKEY1963
Site Agent
Site Agent
Posts: 684
Joined: Wed Jun 13, 2007 11:57 pm

Re: Earth Bonding

by BLAKEY1963 » Sun Jul 05, 2009 12:19 pm

[quote="WHYDIY"]What size cable do I need when installing the primary earth to the stop tap and gas meter to the meter box?

This may have been covered before for that I apologise.

Many Thanks M[/quote]


WHYDIY
EQUIPOTENTIAL bondind to water and gas supply is usally 10 mm2. your electrician . would b glad 2 offer free advice.
BLAKEY1963

kbrownie
Project Manager
Project Manager
Posts: 1995
Joined: Mon Mar 05, 2007 9:36 pm

by kbrownie » Sun Jul 05, 2009 7:12 pm

It's relative to the supply type and the conductor sizeof supply neutral 10mm CSA is normally okay, TT and TN-S system sometimes smaller.

Installing or updating main or suplementary equipotential bonding likely to be okay as far as part p is concerned "grey area!" But I'm sure if this in special location or kitchen it needs notifying or part p electrician employed to do work.
KB

craigmac1878
Labourer
Labourer
Posts: 1
Joined: Mon Jul 06, 2009 3:09 pm

by craigmac1878 » Mon Jul 06, 2009 3:20 pm

Hi, right new to this forum,

Just going for my 17th edition real soon, was just wondering about
an issue with earthing the main stop tap from the fuse board, as I heard in conversation
the other day, that in a new extension build, the main water does not need to b e earthed and that only
The hot and cold pipes and possibly the sink need to be earthed, is this true?

moggy1968
Ganger
Ganger
Posts: 198
Joined: Sat Feb 21, 2009 11:32 am

by moggy1968 » Mon Jul 06, 2009 6:11 pm

complete rubbish I'm afraid!!!
If the rest of the installation is upto 17th edition standards (in the bathroom and kitchen) and certain other criteria are met then there is no requirement for supplementary bonding. your main bonding however always has to be in place and that is connected to the main water and gas, immediately after the supplers meter or, if that is outside, within 600mm of the point of entry into the building.
it sounds like you've got your supplementary (equipotential) and main bonding mixed up.

kbrownie
Project Manager
Project Manager
Posts: 1995
Joined: Mon Mar 05, 2007 9:36 pm

by kbrownie » Mon Jul 06, 2009 7:10 pm

craigmac1878,
I'd like to know where this information came from?
The incoming mains water supply should be bonded to either the MET or the CU depending on your earthing system. This should be within 600mm of entering the property.
No requirement to Supp bond sink.
This is to create an equipotential zone within the property, the water supply could well be delivered to the property via plastic pipework but that is outside equipotentail zone.
The installation will be tied to the mass of earth via MET to earth supply or CU to electrode. If all exposed metal work are connected via bonding this will raise the potential to the same level in the event of a fault.
I can understand it if all the pipe work is plastic but that would then eliminated the risk.