by kbrownie »
Sun Aug 09, 2009 1:04 pm
cball313,
10mm should be plenty big enough.
You have total output value of 2400x2 = 4.8kW
So if the if you intend to run the cooker of 45Amp cooker switch/isolator that's okay.
The circuit will need a 20Amp MCB as that will be enough to power your cookers.
If the cooker isolator was a socket outlet on it, the breaker size will need to be increased to 25Amp MCB
If both cookers are being controlled by the one isolator this needs to be installed so it will isolate both appliance and not just the one.
This isolator should be installed within a minimum distance of 2 meters from the appliances and no closer tham 300mm for any hob.
What you intend to do will need to comply to part p of building regulations and will need notifying to building controls either by you if your DIYing or by your electrician either by self-cert or application.
Some useful links are as follows;
https://www.diydoctor.org.uk/projects/partp.htm
Google "competentperson.co.uk"
regards
KB