LIVE / EARTH REVERSE - 23 volt in live and neutral
Ask questions and find answers to many subjects relating to electrics and electrical work

7 posts   •   Page 1 of 1
danny001
Tradesman
Tradesman
Posts: 47
Joined: Fri Feb 22, 2008 11:35 pm

LIVE / EARTH REVERSE - 23 volt in live and neutral

by danny001 » Thu Aug 06, 2009 6:59 pm

Hi
i have test a wall socket and have found 230volts in the live cable and 230volts in the neutral

i have been told this is called a live/earth reverse

but would like to find out why it is happening or possible causes

thanks

kbrownie
Project Manager
Project Manager
Posts: 1995
Joined: Mon Mar 05, 2007 9:36 pm

by kbrownie » Fri Aug 07, 2009 8:57 pm

How did you measure this and may be able to then spread some light on it!

moggy1968
Ganger
Ganger
Posts: 198
Joined: Sat Feb 21, 2009 11:32 am

by moggy1968 » Fri Aug 07, 2009 10:26 pm

whoever told you that is wrong.
the electricity goes 'out' on the live and 'returns' on the neutral
they both carry current.
a live earth reversal refers to the live and earth (which should not normally carry current) you are talking about the live and neutral (which do)

danny001
Tradesman
Tradesman
Posts: 47
Joined: Fri Feb 22, 2008 11:35 pm

by danny001 » Sat Aug 08, 2009 10:30 am

from the consumer unit to the shed there is only one cable which leeds to a double socket,
it is just used to plug in the jet washer for the car
one day it was not working
i used one of the plug testers and on the diagram it says its a live/earth reverse
also opened the socket up,
with a fluke T100 tester found that between the earth and live 230 volts and the same between the earth and neutral

i cant see how this has happened, have spoke to someone who said its the live and neutral have joined in the cable, so any ideas of the cause would be a great help before i did up garden

thanks D

danny001
Tradesman
Tradesman
Posts: 47
Joined: Fri Feb 22, 2008 11:35 pm

by danny001 » Sat Aug 08, 2009 10:35 am

HI,
nothing works when pluged into this socket

i also tested a socket in the kitchen which just has the power in the live side not neutral, this is working

moggy1968
Ganger
Ganger
Posts: 198
Joined: Sat Feb 21, 2009 11:32 am

by moggy1968 » Sat Aug 08, 2009 10:04 pm

if your live and neutral join together you have a dead short and it will blow a fuse or trip an MCB. most likely thing off the top of my head is a neutral has come adrift bihind a faceplate somewhere or in the consumer unit.

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Sun Aug 09, 2009 12:14 am

it seems you have lost the neutral connection somewhere, possibly at house supply end, check connections first,