by htg engineer »
Mon Aug 10, 2009 8:23 pm
Before we go down the route of wiring, can you explain the set-up.
For a standard underfloor system, the two port valve would be to isolate this section when the stat reaches temp - or is turned down. The way you're going to set it up, a two port valve is no use - you need a three port valve, where AB will be flow A will be central heating and B will be underfloor heating. And the wiring wont be as simple as you think.
The manifold pump ?? when you put power to the combi the pump will run - why do you need another pump ? not needed, if you get one pumping against the other - one will pack up.
Why do you want the conservatory heating on and not the rest of the house ?
The easiest set-up, is tee into flow and return like you would if installing another radiator - connect two port valve with thermostat, stat down or temp met - valve closes, undefloor heating off. But it will only work if the heating is on for the rest of the house.
htg