RCCB vs RCD
Ask questions and find answers to many subjects relating to electrics and electrical work

3 posts   •   Page 1 of 1
Neil Copeland
Labourer
Labourer
Posts: 2
Joined: Wed Aug 19, 2009 10:30 pm

RCCB vs RCD

by Neil Copeland » Wed Aug 19, 2009 11:10 pm

Please advise if an RCCB provides the same protection as an RCD and if so can it be used for electric shower installations. Thanks.

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Thu Aug 20, 2009 7:58 pm

Rccb=residual current circuit breaker
RCD=residual current device
GFCI=ground fault circuit interupter-(U.S.)
DI = Differentia Interupter -(SPAIN)

Same thing, different terminology
your part P electrician should know this,
regards Sparx

moggy1968
Ganger
Ganger
Posts: 198
Joined: Sat Feb 21, 2009 11:32 am

by moggy1968 » Fri Aug 21, 2009 12:43 am

worth noting though that those do not give overcurrent protection, which you must habe as well. that take the form of an MCB (Main Circuit Breaker, usually now fitted with an RCD unit protecting a bank of MCBs) or RCBO (RCD MCB combined in a single unit)

3 posts   •   Page 1 of 1
It is currently Sat Jan 18, 2025 12:34 am