Need your input on this
Last three days my RCD has been triping up upto 8 times per day.
The fuse that is going seems to be the downstairs ring [sockets] It has all the tv, fridge, tumble dryer, washing machine etc on it. But its only been happening for last three days. The wiring is 3 years old and was certified and passed
Today I called the homecare guys out and the spraky says that he tested the RCD at 30mA which is fine and he said the load on the circuit was 19.5? He said a reading of 13-14 and it tripping would be cause for concern but 19.5 is bang in the middle and this is whats causing the issue - ie too much on the ciruit. He did checks on the wiring and board and said all was ok and then recommended breaking up the sockets and putting in a RCBO or something? But i cant understand why it just happens in the last few days. Nothing new has been added.
Does this make sense or is he bull****** me?
thanks guys
Jay