by kbrownie »
Tue Oct 06, 2009 10:11 am
Sounds like you have had mister/missus Crazy doing the circuits.
I'm assuming these are all radial circuits.
So what cable size are they currently and what is the fuse rated at?
It is possible to link them up using two of the sockets already installed as outgoing and incoming legs.
If your intention is to create a ring.
The cable size for ring circuits would be suitable to 2.5mm cable and a breaker size of 32A.
Now linking the other sockets could cause a problem, if the junction boxes are to be within ceiling void or under floors. Most types of joints between cables must be easily accessible for inspection and testing purposes.
Crimp and solder joints can be used which will need specialist tools and specialist knowledge.
I'd be thinking off going directly in to the socket boxes and linking between boxes.
Depending on the age of your installation you may end up with two different types of core colours as they changed about 4 years ago and a notice should go on the Consumer Unit stating this.
https://www.diydoctor.org.uk/projects/wirecolours.htm
You will also need to install RCD protection as that is now a requirement.
Saying all this, I would consider rewiring the circuit all together,
but your problem will be that as soon as you install a new protective device breaker/fuse/rcbo/rcd.
It then becomes a new circuit and must be notified to Building Controls.
If you DIY it they will charge you a fee of £135 for you to install it, then you will also need to buy materials needed to do the work.
https://www.diydoctor.org.uk/projects/partp.htm
So again maybe worth considering getting a registered electrician in.
Google "competentperson.co.uk"
Bet you thought it would be easy, but hope this helped and gave you an insight on what you'd need to do any more question please reply.
Regards
KB