Gas fire poor heat output
Information, help and advice on many gas related subjects from gas fires to domestic appliances

3 posts   •   Page 1 of 1
chub0121
Labourer
Labourer
Posts: 2
Joined: Sat Oct 31, 2009 4:52 pm

Gas fire poor heat output

by chub0121 » Sat Oct 31, 2009 5:47 pm

hello,
I have a Valor Bolero inset gas fire,fitted ten years ago.A Valour engineer serviced it a year ago.I mentioned to him the heat output was markedly less than when it was new.He said after servicing,the fire was within the makers spec for performance.i had the idea of trying to check myself.Imeasured the gas used in exactly one hour, on full.by reading the meter.
I used the formula :Cu Ft gasX3.6=Kw
my result was3.3Kw
I see the fire spec says max input 6.8Kw, min input 2.2kw

Am I right in thinking ,based on this result the fire is not working properly?

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Tue Nov 03, 2009 8:08 pm

Get the fire serviced, injectors and fire tap stripped and cleaned, if that doesn't work - replace the fire tap.


htg

chub0121
Labourer
Labourer
Posts: 2
Joined: Sat Oct 31, 2009 4:52 pm

Gas fire poor heat output

by chub0121 » Wed Nov 04, 2009 9:38 am

Heating eng.
Thanks very much for the info,Iwill act on it.