RCD tripping no apparent reason

by Blazeboy » Sat Nov 14, 2009 5:39 pm

We have had a long standing problem with our electrics tripping but no particular circuit just the mains switch on the board.
It can go for months without a problem and then trips when we only have a fridge and freezer on. Normally the weather is not a factor it can be hot or dry or wet. Today however, it has been very wet and windy and it has tripped 3 times.
When it tripped today we had the fridge and freezer on and the heating.
Any ideas?
Thank you very much in advance.

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Sat Nov 14, 2009 8:15 pm

Hi,
presume main switch is an RCD which means the problem is an earth leakage fault.
As it is so intermittant the only way to find fault which may be a combination of small leakages is to get the circuits tested with an insulation tester and earth leakage clamp meter.
Not the sort of thing anyone but a leckie would have so afraid it's down to professional to check out,
regards sparx

Blazeboy
Labourer
Labourer
Posts: 2
Joined: Sat Nov 14, 2009 5:30 pm

by Blazeboy » Sat Nov 14, 2009 9:32 pm

Many thanks for advice.