Warm air boiler booming when ignites
Information, help and advice on many gas related subjects from gas fires to domestic appliances

5 posts   •   Page 1 of 1
spinkox
Apprentice
Apprentice
Posts: 11
Joined: Wed Feb 04, 2009 6:14 pm

Warm air boiler booming when ignites

by spinkox » Thu Nov 12, 2009 11:46 am

My father has a Lennox Duraglass G11 warm air heating boiler and occasionally when it ignites it makes a massive boom. I thought he was exaggerating til I heard how bad it was. He has had an engineer around but it has never been solved. Any ideas??

steve

DEEARR2
Ganger
Ganger
Posts: 160
Joined: Sun Oct 12, 2008 9:49 pm

by DEEARR2 » Wed Nov 25, 2009 8:34 pm

Had similar problem with a Lennox Unit. Fault was caused by delayed ignition where the main gas was not getting to the constant pilot quick enough and causing a build up. Finally modjfied the unit by relocating the pilot assembly into the centre of the main burner bar. No explosions since.

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Fri Nov 27, 2009 8:53 am

Possibly just needs the pilot cleaning, if the gas valve opens and the pilot flame is poor = explosive ignition.


htg

spinkox
Apprentice
Apprentice
Posts: 11
Joined: Wed Feb 04, 2009 6:14 pm

by spinkox » Mon Dec 07, 2009 11:14 am

Thanks. . .

It has been looked at by an engineer so I suspect the pilot is clean but he has run out of ideas. How easy is it to relocate the pilot assembly to the centre??

steve

DEEARR2
Ganger
Ganger
Posts: 160
Joined: Sun Oct 12, 2008 9:49 pm

by DEEARR2 » Tue Dec 08, 2009 7:14 pm

The modification is quite simple. If your engineer buys a 6mm Bundy kit,
which comprises of a length of 6mm soft alloy pipe and a selection of fittings, it is then a matter of re-location of the pilot assembly with a couple of screws and repipe back to the gas valve. GSR engineer is a must.