Boiler and Pump keep shutting down

by Penn » Wed Dec 02, 2009 12:31 pm

My System I believe is convetional and comprises of:
Boiler - Potterton Suprima
Programmer - Potterton EP2002
Valve - Potterton MPE322
Pump - MYSON Compact CP3
Thermostat - Drayton Digistat +3


The problem is that when heating is called for the boiler and pump cut in for 5 mins and then both cut out for 5 mins even though the radiators are only luke warm, this cycle appears to repeat all the time the thermostat is calling for heating. While the pump and boiler are running the heating LED on the valve turns from slight glow to bright but as soon as the bioler cuts out the pump stops and the valve LED returns to slight glow.

plighto
Labourer
Labourer
Posts: 1
Joined: Wed Dec 02, 2009 8:14 pm

Boiler keeps cutting out

by plighto » Fri Dec 04, 2009 7:50 pm

I have a similar problem, but my system is an (old) Potterton Netaheat boiler running hot water and radiators.

The thermostat is calling for heat but the radiators are lukewarm. The pump is running continually and the boiler fires up but runs for only a short time. Then the flame shuts off but the fan continues to run.

The radiators are all bled and working fine. The pump seems OK and is quite new.

It's an intermittent fault. Sometimes it runs OK. I wonder if it could be the boiler thermostat misreading the circulating water temperature?

Any suggestions? What to do?

DEEARR2
Ganger
Ganger
Posts: 160
Joined: Sun Oct 12, 2008 9:49 pm

by DEEARR2 » Fri Dec 04, 2009 8:49 pm

The Potterton Suprima has a history of faulty PCBs on boilers around 4 years old which was hightlighted on the watchdog program. It would be worth having an engineer check it over and have the fault identified. The pcb is the worse case senario as they are quite expensive.

Penn
Labourer
Labourer
Posts: 3
Joined: Wed Dec 02, 2009 11:37 am

by Penn » Sun Dec 06, 2009 12:11 pm

Reply to DEEAR2

Have read many reports about the Watchdog programme problems but mine sounds slightly different (incidently my boiler is about 9 years old).

Could you just confirm that all the while the programer and thermostat are calling for heating the pump should be running.

rosebery
Project Manager
Project Manager
Posts: 2021
Joined: Wed Sep 26, 2007 9:55 pm

by rosebery » Sun Dec 06, 2009 8:57 pm

Is the water actually circulating? Its more likely that it isn't and that the boiler stat is working perfectly well and is shutting down the boiler when it reaches the required temperature which it will if the water isn't circulating.

Look for a blockage - where the feed from the F&E tank joins the primary is favourite.

Cheers

Penn
Labourer
Labourer
Posts: 3
Joined: Wed Dec 02, 2009 11:37 am

by Penn » Mon Dec 07, 2009 10:20 am

Reply to Rosebery

No the the water is not circulating but that is because both the pump has stopped and the valve has shut even though the heating system is on and the thermostat is calling for heating. When I first noticed the problem I just thought it was just the boiler shutting down on the overheat stat.

At the moment the downside of this problem is that the radiators take at least 40 mins to come up to temperature when the heating starts. After that even though the bioler cycles the heating works well enough.

rosebery
Project Manager
Project Manager
Posts: 2021
Joined: Wed Sep 26, 2007 9:55 pm

by rosebery » Tue Dec 08, 2009 8:03 am

Penn

My question was is it circulating BEFORE the boiler shuts down and the pump stops?

Thats the point. If there is no circulation (when the pump is running) then sooner orlater the boiler stat will shut the boiler down and if there is no overrun circuit the pump will stop at that time as well.

I think you've got a blockage in your system

Cheers

DEEARR2
Ganger
Ganger
Posts: 160
Joined: Sun Oct 12, 2008 9:49 pm

by DEEARR2 » Tue Dec 08, 2009 7:24 pm

When the signal from the programmer and thermostat is sent to the boiler the pump is signalled to run and will only shut down when the programmer times to the off period and heat in the boiler is dissapated.

johnsmith0774
Labourer
Labourer
Posts: 2
Joined: Tue Dec 08, 2009 9:36 pm

by johnsmith0774 » Tue Dec 08, 2009 9:37 pm

hello,

this same thing happened to me and i found out the answer of how to fix it. not sure if this is a current thread though so wont write it all now. if it is let me know and ill give you the details.

rosebery
Project Manager
Project Manager
Posts: 2021
Joined: Wed Sep 26, 2007 9:55 pm

by rosebery » Fri Dec 11, 2009 9:08 pm

"When the signal from the programmer and thermostat is sent to the boiler the pump is signalled to run and will only shut down when the programmer times to the off period and heat in the boiler is dissapated."

Not if theres no overrun circuit though.

Cheers

mpereira
Labourer
Labourer
Posts: 1
Joined: Sun Dec 13, 2009 7:10 pm

by mpereira » Sun Dec 13, 2009 7:14 pm

[quote="johnsmith0774"]hello,

this same thing happened to me and i found out the answer of how to fix it. not sure if this is a current thread though so wont write it all now. if it is let me know and ill give you the details.[/quote]

Hi,

Would appreciate knowing how you fixed this particular problem, I am having the same issue with my 'very old' central heating system and would like to be able to find a resolution to the problem.

Please post your solution.

Many thanks.

BERRY1
Labourer
Labourer
Posts: 1
Joined: Thu Mar 08, 2012 10:02 pm

Potterton EP2002

by BERRY1 » Thu Mar 08, 2012 10:26 pm

Hi Penn

You had a problem with your Potterton EP2002 cutting out after 5 minutes with your radiators only getting luke warm. Did you find a resolution for this?