[quote="Dante"]it's a combi system and as far as i no I don't have to alter pressure it was serviced 10 months ago. waterboard switched the water off 5 or 6 months ago which, may have drained the system or let air in. other than that sounds like i may have to pay for help.[/quote]
What is the reading on the pressure gauge at the boiler? This should be between 1 & 1.5 bars.
A combi (sealed) system should top-up in seconds, not days as your first post stated.
Locate the system filling loop and re-pressurise the system to 1 bar, vent one radiator at a time and keep re-checking the system pressure. When all radiators are full re-visit the boiler and make sure the system pressure is between 1 & 1.5 bar.