by pjcomp »
Sun Jan 10, 2010 12:23 pm
[quote="BLAKEY1963"]MILKSLUG
Above your door , areas called safe zones should have
been taken into account when your wiring was installed.
FROM the ceiling down a distance of 150mm ( 6 inches )
across the whole wall , any thing inside this area should
not contain any cables.
[/quote]
This is WRONG - the "safe" zone 150mm down from the ceiling is where it is "safe" to install wiring. Wiring Regs 522.6.6(v): "A cable concealed in a wall ... shall be installed in a zone within 150mm from the top of the wall ...or within 150mm of an angloe formed by two adjoining walls".