Hi all,
Only basics now i'm afraid.
Main house max demand 210a with diversity.
Granny annexe 115a with diversity.
I recommended extra phase to supply annexe as it will be ran as a new house by mother-in-law.
Not happy with that, they had second opinion and now have split tails with sub CU supplying annexe 25m away on 16mm2 T&E.
So 100a supply cutout, 114a 25mm2 tails, splitter box 100a max, meter 100a and overhaed cables 100a (as per e on) supplying two houses. Combined max demand after diversity 325a. Don't like what has been done. LABC inspecting and testing as I have walked. My concern is a family being cooked due to overloaded supply cables, tails, meter, splitter box.
I know this is basic but I can't write it all again as my will to live has been tested already.
Any opinions are very welcome.
Kind regards
Jackhawk