Sat May 29, 2010 7:24 pm
If it's pressurised then airlocks/air wont be a problem.
You wont know what you need to do, until you drain the system, and check the condition of the water.
I would advise, draining, removing all radiators and flushing through with hosepipe. Turn off all radiator valves, open/connect filling loop (not fully, as it will fill too quick and operate PRV) - open each valve one by one and allow to flow into a bucket or down a hosepipe.
If the water is clear refill and add inhibitor - such as Sentinel X100.
If the water is still dis-coloured I would add a system cleanser. And repeat above process after a few days.
Bearing in my you nearly always get abit dis-colouration of the water.