Hi, I do lots of work on caravan parks, many different ways of supplying vans in use.
You mention outside & inside RCD's. where is the outside one?
Some are in distribution cupboards a distance from the van rather than at a local hook-up box.
If so the internal RCD will only see leakage from inside the van but the remote one will see the same plus any leekage from the cable between them and will therefore usually trip first.
The lack of discrimination Ericmark refers to.
Most supplies are underground and could have had minor damage from an awning peg say.
One site I deal with has RCBO's in boxes giving both Earthleakage and overcurrent protection to each supply so if they trip it is impossible to tell which caused the trip, most vans only have RCD as main switch with a couple of MCB,s for each circuit protection.
The supply device is rated 16A/30mA but the vans have 6A plus 32A circuits.
Something for your leckie to look into...