SWA TO CONSUMER UNIT
Ask questions and find answers to many subjects relating to electrics and electrical work

4 posts   •   Page 1 of 1
PHILSTER
Labourer
Labourer
Posts: 2
Joined: Tue Dec 14, 2010 8:34 am

SWA TO CONSUMER UNIT

by PHILSTER » Tue Dec 14, 2010 8:41 am

HI
CAN ANYONE TELL ME IF SWA CABLE NEEDS TO TO GO TO A JUNCTION BOX FIRST THEN TWIN AND EARTH TO CONSUMER UNIT?
CONSIDERING EARTHING OF SWA USING THE CORRECT GLAND I PRESUME THIS IS THE WAY TO DO IT? (AND NOT SWA DIRECT TO CONSUMER UNIT)
CHEERS
PHILSTER.

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Tue Dec 14, 2010 9:33 pm

hi, no reason other than visual asthetics not to go direct to con.unit. even a plastic one if using correct gland plate or better still 'Piranha-P-Nut' earthing nut with tail
(google 'piranha earth nuts)
regards Sparx

ericmark
Project Manager
Project Manager
Posts: 2870
Joined: Fri Oct 02, 2009 9:49 pm
Location: Llanfair Caereinion, Mid Wales.

by ericmark » Tue Dec 14, 2010 10:07 pm

As Sparx says you can go direct even into plastic however I have in the past found problem where the SWA has put strain on the plastic and warped it. I have used either an adaptable box or a metal clad socket box with plain lid and a tube nut or two to join the box to consumer unit purely to remove strain from consumer unit. Normally I would then take the inner onto consumer unit stripping back only part inside the consumer unit.
The earth is a big issue and Sparx has likely best option. Do remember to used brass earth bolts not steel on banjo if that is main earth. If using a core as an earth not really a problem. Also remember 4mm is min size for external earth links.

PHILSTER
Labourer
Labourer
Posts: 2
Joined: Tue Dec 14, 2010 8:34 am

by PHILSTER » Thu Dec 16, 2010 4:11 pm

THANKS VERY MUCH FOR YOUR HELP!!
HAPPY CHRISTMAS

PHILSTER