Help. I seem to have a strange problem. I read all the other posts/blogs I could find but none seems to describe my issue..
Problem Description: About a week ago I came home to a cold house & spotted that the lights were out on the CH Programmer (which was a Siemens RWB9). The clock display was still showing, but it is battery backed-up. Suspecting a fuse-blow, I isolated the system, then replaced the 3A fuse in the spur feed. I turned back on but still (apparently) nothing. Other things in the same ring main all working AOK, so I knew it wasn't a trip in the distribution board.
I checked out the two fuses (old one and the new one I'd just put in) using a multimeter, and sure enough both were blown.
Suspecting a fault downstream of the programmer, I selected 'Off' for both CH and HW programmes, and tried another new 3A fuse (fortunately I had a pack of 5 fuses to hand). Again an instant blow.
Maybe at this stage a brief system description is called for:
Basically, it is an S-Plan system, with an indirect/unvented HW cylinder and unvented CH, plus rather old Glow-worm freestanding boiler (not very green I know, but it works reliably and the heat it gives off contributes to space heating the basement where it is sited). Additionally, I have a recently installed underfloor heating loop for the kitchen. This is paralleled off the existing system, with its own controller (ie is completely independent of control from the original CH programmer, except of course it takes its feed from the same 3A spur). So, on the primary boiler flow leg there are three 2 port valves in parallel... one each for UFH , DHW and CH/rads. They are wired in such a way that when energised any one of them will open the valve and call the boiler and both pumps (the UFH system has its own circulating pump which runs every time the main pump runs; if the UFH is not calling for heat then its 2 port valve remains shut and the water in the UFH loop circulates without further heating; this seems a bit strange but is the strategy specified by the manufacturer (LK)).
The 2-port valves are 2 x Honeywell 272848's (for HW and CH) and a Myson 'Power Extra' (for UFH).
The HW cyl has a thermostat in series with the 'call' feed from the programmer; the CH has a programmable room stat in series with the 'call' feed from the programmer too, and I control the CH on/off from here.. the programmer being always set constant 'on' for CH. DHW is normally set for one hour each evening only.
The reconfigured system (ie with added UFH) was commissioned about 4 weeks ago. The Sparkie installed a new wiring centre and completely renewed all wiring associated with the system, downstream of the fused spur. Since everything had run faultlessly for 4 weeks, I'm disinclined to suspect an installation wiring fault (I have checked over all the wiring that is visible and confirmed it is (a) correct and (b) no obvious mechanical damage exists. I have to say the inside of the wiring centre is a bit of a rat's nest, but nonetheless, everything goes where it should go.
Now back to the problem description (still with me??)...
So. Suspecting the programmer pcb had somehow gone short-circuit, I decided to run the system temporarily without it. Having isolated the supply once more, I disconnected the L/N feed in the programmer backplate and 'parked' them in a terminal block. Then I linked the CH call line to Live ( via a link wire I added in the wiring centre). I left the HW call in the programmer backplate - so effectively disconnected), as I could manually top up the HW by operating the lever on its 2 port valve (I have a temperature readout from the top of the HW store, so can monitor this and shut off the heat again when it reaches temp). Fit new 3A fuse; turn on.. Bingo - everything works correctly; warm house again :)
So. Conclusion: Programmer is shot. Right? Wrong!
A couple of days later, I went out and bought a new programmer; a Horstmann C27 (best price from Screwfix, and same backplate as the old one; Simples).
Half an hour to reconnect all the wiring correctly - ie undo my temp arrangement described above, then plug the new programmer onto the backplate and turn on the mains. Display lights up OK. Select CH 'on' - CH works; select HW 'on' - fuse blows again!!
OK, I know what you are thinking.. same as me: the HW 2 port valve, or tank stat must be the problem. The tank stat checked out OK (well open cct when turned 'up' and then 'clicked'/zero resistance across contacts when turned 'down')
So I took the actuator head off the 2 port valve and disconnected it from the system. It just so happens I have a spare (I won't explain why: too boring), but (being an engineer) I decided to put the multimeter across the various wires of the old and new valve actuators - to see if I could demonstrate there was a problem with the old one. Since both actuators read out exactly the same resistances across/between all the various leads, I suspected no fault (the new valve is only 4 weeks old after all). So I wired the actuator (brown/blue/earth) into a 13A plugtop (yes, with a 3A fuse fitted) and energised it. The motor worked fine and the microswitch contacts (grey/orange wires) closed OK when it had gone full travel; de-energised and all returned to normal/closed position.
Anyway, being bored with it all by now and running out of time that day I decided to reinstall the HW 2 port valve actuator into the system, but to leave it disconnected. To prove a further point with the system, I wired it all back in, but left the brown feed wire to the 2 port valve disconnected in the wiring centre.. so that the tank stat was in circuit.
On reconnecting the programmer, all was fine (and when I selected HW the 'on' lamp lit, but of course nothing happened as the circuit was incomplete).
So. It seems there is a fault in the HW circuit somewhere after all. Until - later that evening - suddenly I noticed the house was getting cold. Yes: the fuse had blown again.
And it seems the programmer has blown again too (to be certain of this, I took the CH/HW 'on' wires out of the backplate, so when I turned on having replaced the fuse all I was doing was energising the programmer, and the fuse blew instantly. Of course the rest of the system (2 port valves, UFH, pumps) was still connected too via the wiring centre, but if I isolate the programmer L/N feed and link the CH to permanently call heat (via the room stat), as I did before, then all works fine and has continued to do so for days now.
HELP!
I cannot afford to keep blowing-up programmers to try and solve this. So far I have got through about a dozen 3A fuses, but that's OK as they are cheap enough. And I can survive as I am for a while, but I'd like full auto control back ideally.
Does anyone have a clue??? Should I try bench-testing the programmer(s)?
Given the system has two pumps, 3x 2-port valves, plus the boiler, is a 3A fuse sufficient? Can interactions between the system components cause some kind of current surge if say all the valves were to work together, coincidentally? If so, why don't fuses bliw with the programmerr out of circuit? What is causing the programmer to go pop??
Thanks for your patience reading this; I appreciate any feedback.