by ericmark »
Fri Feb 18, 2011 6:44 pm
I would agree that with an old installation damp and dust can cause tracking and when dry the fault can clear it's self. However often the tracking causes a deposit of carbon and even when dried out the carbon will still allow current to flow even when dried out.
If it is tripping a RCD then it could be very little current flowing and it will likely mean the switch boxes need cleaning of any dust or plaster drips.
However if it is the MCB tripping then the situation seems more serious and really unlikely to be caused by wet plaster.
The fact that some time elapses between switching on lights and tripping I would think it is more likely caused by some thing heating up. And I would be looking at an florescent lamps.
There is an exception where mineral insulated cable is used. But unless your living in a stone cottage or a listed building where there is a fire worry it is unlikely any normal house will be wired with mineral insulated cable.
The meters used to detect the problems are not cheap and use 500v to high light problems so as already said it's time to get electrician back and tell him to sort it. It is not a DIY job as most DIY people will not have the 500 volt ohm meter required. (Often called a megga) The electrician should be able to tell you how many meg ohms it is to earth which means he has measured not guessed.