in-line shower fan

by moley » Mon Mar 28, 2011 6:34 pm

hi i have just got a in-line shower fan with timer do i need to use wire size 1.0-1.5 cable the same as wire for lights thankyou

ericmark
Project Manager
Project Manager
Posts: 2870
Joined: Fri Oct 02, 2009 9:49 pm
Location: Llanfair Caereinion, Mid Wales.

by ericmark » Tue Mar 29, 2011 7:41 am

Cable sizes are selected according to:-
Manufactures recommendations.
Earth loop impedance.
Volt drop.
Protection device size.
Environment i.e. insulation in walls.
Likely 1.5 mm sq will comply but until you have measured the earth loop impedance for example you will not know.

Since you will first need to inform LABC and they will want to either see your test results and/or test themselves with a bathroom there are no short cuts.

Likely getting an electrician who is a member of a scheme will be cheaper than DIY.