This is a well known and documented problem.
Guidence note 1 says "live cables (inc Neutrals)of the same circuit may cause overheating if they enter a ferromagnetic enclosure through different openings"; & refers to reg sect 521.
Red book 521.5.2 ..."The conductors of an AC circuit installed in a ferromagnetic enclosure shall be so arranged that all line conductors and the neutral, if any, & the appropriate protective conductor are contained in the same enclosure.
Where such conductors enter a ferrous enclosure, they shall be arranged such that the conductors are only collectively surrounded by ferrous metal."
So it's in the regs; even if obliquely worded.