Ariston ACO 27 RFFI condensing boiler
Help and information on all topics relating to your central heating, air conditioning and ventilation issues.

3 posts   •   Page 1 of 1
brian mac
Labourer
Labourer
Posts: 2
Joined: Tue Oct 25, 2011 12:26 am

Ariston ACO 27 RFFI condensing boiler

by brian mac » Tue Oct 25, 2011 1:31 am

Hello One and All,
I have an Ariston condensing boiler providing CH and and Domestic Hot Water(DHW) using a hot water cylinder.
When the boiler "fires up" the system makes a series of,what can be best described as loud gurgles and pops. Could this be air? Also the boiler pressure guage reads zero despite the pressure gauge on the cold water header feed to the system reading 1.5 bar.
At present both CH and DHW are both operating OK despite start up noises although rads appear to need balancing.
I have read previous threads but they appear to be mainly for combi's - can anyone please shed any light on best approach.
Regards Brian Mac

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

Re: Ariston ACO 27 RFFI condensing boiler

by sparx » Thu Oct 27, 2011 8:30 pm

Hi,
you may have answered your own question!
The pressure gauge should read between 1-1.5 bar, there should be a filling loop with the boiler, see hand book, which if you don't have one it is available as a down load.
or tech help on 0870 241 8180 or customer help on 0870 600 9888.
regards

brian mac
Labourer
Labourer
Posts: 2
Joined: Tue Oct 25, 2011 12:26 am

Re: Ariston ACO 27 RFFI condensing boiler

by brian mac » Tue Nov 01, 2011 12:47 am

Thanks Sparx. Will look in handbook.

3 posts   •   Page 1 of 1