Atticus Finch wrote:I'm sorry to say this, but that looks a very second rate job.
by Atticus Finch » Sun Jul 01, 2012 10:43 am
plumbbob wrote:Pipe diameters are wrong and what are all the service valves for???
by georgepaterson5 » Mon Jul 02, 2012 8:06 pm
by plumbbob » Tue Jul 03, 2012 9:41 am
by Atticus Finch » Tue Jul 03, 2012 10:48 am
plumbbob wrote:I am not surprised it is pulling in air because the two connections to the expansion tank are wrongly on different sides of the pump.
by plumbbob » Tue Jul 03, 2012 5:23 pm
Atticus Finch wrote:Having the vent and feed on opposite sides of the boiler was fairly normal with cast iron HE's as the pressure drop through the boiler was negligible.
Atticus Finch wrote:As well as moving the feed pipe connection, a second motorized valve is required in the HW circuit and a cylinder stat. In addition a new programmer is probably required so you have independent control of CH/HW times and temperatures. I have shown the changes in this diagram. And get rid of the plastic pipes/joints.