Lenth of condensation pipe from a boiler

by collectors » Sat Jun 01, 2013 1:32 pm

Hi, we are fitting a boiler & are about to fit a 22mm condensation pipe from the boiler to a waste pipe in the bathroom, but the length of run is around 11 meters with a nice slope. What is the maximum length this can be in 22mm?.
The only info with the boiler is that on a long run, increase the pipe to 32mm.
But! what is classed as a long run?

Thanks

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

Re: Lenth of condensation pipe from a boiler

by htg engineer » Thu Jun 20, 2013 10:02 pm

You must be Gas Safe Registered to install a gas appliance. Employ a gas safe registered engineer to install the boiler.

collectors
Foreman
Foreman
Posts: 485
Joined: Mon Dec 01, 2008 7:26 am

Re: Lenth of condensation pipe from a boiler

by collectors » Fri Jun 21, 2013 7:39 am

The boiler is being fitted by a gas safe engineer. We was helping by getting some of the pipework to the boiler area. The engineer said he will call the manufacturer & this is the answer they gave & found the reply very odd.

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

Re: Lenth of condensation pipe from a boiler

by htg engineer » Fri Jun 21, 2013 6:50 pm

11m is a very long run, I wouldn't install 11m of internal condensate pipework, you need 45mm per metre fall. By the 11th meter you'd need to be 19.5" lower than the 1st metre, which you will not get under a floor.

You need to look for the shortest route, 3m or so. Fit a tundish to help with flow, make sure you have minimum of 45mm fall otherwise they can back up and cause costly repairs to boiler components. If you cannot reduce to a 3m length, then you need to look as pumping the condensate.

htg

collectors
Foreman
Foreman
Posts: 485
Joined: Mon Dec 01, 2008 7:26 am

Re: Lenth of condensation pipe from a boiler

by collectors » Sat Jun 22, 2013 8:56 am

Hi, thanks for getting back. The boiler is a wall mounted glow-worm sited on the gable end wall in the loft of a bungalow. For the small difference in price we have put in 32mm waste from the outlet in the bathroom which is 9m away & just made the last 500mm to the boiler in 22mm pipe. The main reason for not going the shorter route of around 5m's is the amount of times we have had customers & friends having the condensation pipe freeze in the winter, even though some were lagged.
We had -14 here a few times last year.
But will pop in tundish to help.

Thanks

Chris