Replacing old Downlights With 240v Downlights - are They Direct Swap?

by sfrazi » Sun Nov 24, 2013 2:47 am

We have completely gutted our ensuite, At the moment there are 4 mr16 12v 50w downlights dangling down. These need replacing as, at some point whilst removing ceiling for renovations, some of the lighting fixtures were taken off and have been lost in the rubble.

I would like to replace these lights with 4 mains 240v downlights as I believe there are more LED variety with mains GU10 lights as opposed to low voltage mr16.

My question is would is be a simply swap. i.e taking lighting fixture and transformer off and replace with mains voltage lighting fixture or do I need to replace the existing wiring as well? I ask this as the existing wiring consists of thin white wires and I thought it would have been the standard grey thicker lighting wire.

DIYorNot
Tradesman
Tradesman
Posts: 27
Joined: Sat Nov 02, 2013 6:05 pm

Re: Replacing old Downlights With 240v Downlights - are They Direct Swap?

by DIYorNot » Sun Nov 24, 2013 4:11 pm

You will need to install IPX4 rated light fittings or better. It is prefereable to use a SELV transformer to feed the lights if in an area that it likely to be splashed by water or above where you're showering.

http://www.islandbathrooms.co.uk/blog/what-are-bathroom-electrical-zones-

The thin white wires which you are referring to are heat resistant wires which connect between the connection terminals and lamp holder.

You should be looking at good 6 or 7W lamps to replace a 50W halogen.

sfrazi
Apprentice
Apprentice
Posts: 17
Joined: Thu Jun 30, 2011 1:55 pm

Re: Replacing old Downlights With 240v Downlights - are They Direct Swap?

by sfrazi » Sun Nov 24, 2013 7:24 pm

Just noticed if I pull a bit more than I find the usual grey wires.

I will therefore get the mains voltage fixings that are suitable for bathrooms i.e. IP65/66.

One more question...do I need the fire rated ones or does that not matter since I am buying ones suitable for bathrooms?

DIYorNot
Tradesman
Tradesman
Posts: 27
Joined: Sat Nov 02, 2013 6:05 pm

Re: Replacing old Downlights With 240v Downlights - are They Direct Swap?

by DIYorNot » Sun Nov 24, 2013 8:53 pm

Fire rated fittings were more of an issue with halogen lamps however, that's not to say that LED lamps don't catch fire.

You need to establish whether the ceiling/void above provides a fire barrier and if it does, then you need fire rated fittings.

The grey cable you are referring to is known as twin and earth and should have solid phase (live), neutral and earth wires inside.

ericmark
Project Manager
Project Manager
Posts: 2869
Joined: Fri Oct 02, 2009 9:49 pm
Location: Llanfair Caereinion, Mid Wales.

Re: Replacing old Downlights With 240v Downlights - are They Direct Swap?

by ericmark » Mon Nov 25, 2013 12:45 am

The fire rating is to stop fire going through the holes you cut and not to spot fire created by the light. So it's not an electrical requirement but depends on the building.

230vac is classed as low voltage 12 volt is extra low voltage. Unlikely you need IP65 the zone dictates the IP rating.

701.512.2 External influences
Installed electrical equipment shall have at least the following degrees of protection:
(i) In zone 0: IPX7
(ii) In zones 1 and 2: IPX4.

So likely IP54 is good enough but should say on packaging suitable for bathroom since lights are now required to be RCD protected you may need to all this as not replacing like for like. However with RCD protection should water get in the lamp it should fail safe.

If you are going through a building inspector best is always to list what you intend to do. Better that he says no before rather than after but the inspectors with my mothers bathroom did not look at the job they took my installation certificate and just issued the completion certificate.

Most areas of UK bathroom work is still notifiable but in England it depends I think on the zones now but I live in Wales so no change for me. You will need to check yourself.

The problem with most DIY is to fill in the installation certificate you need to enter the readings from the test meters and the meters are expensive as are the LABC fees so if you want to be legal then likely cheaper not to DIY.

diydoctor6
Ganger
Ganger
Posts: 145
Joined: Thu Feb 05, 2009 1:54 pm

Re: Replacing old Downlights With 240v Downlights - are They Direct Swap?

by diydoctor6 » Mon Oct 30, 2017 2:56 pm

We've put a handy table on this project so you can easily see the IP rating requirements for each zone in your bathroom safety zones:

https://www.diydoctor.org.uk/projects/ba ... -zones.htm

Hopefully this makes it a little easier to see what you need.