by ericmark »
Sat Jul 19, 2014 9:33 pm
SECTION 702
SWIMMING POOLS AND OTHER BASINS
Reading this there seem nothing different between permanent and temporary installations.
Zone 1 and 2 no 230 volt permitted.
NOTE: Where the supply to the swimming pool is part of a TN-C-S system it is recommended that an earth mat or earth electrode of suitably low resistance e.g. 20 ohms or less. be installed and connected to the protective equipotential bonding.
702.55.1 Current-using equipment of swimming pools
In zones 0 and l, it is only permitted to install fixed current-using equipment specifically designed for use in a swimming pool, in accordance with the requirements of Regulations 702.55.2 and 702.55.4.
Equipment which is intended to be in operation only when people are outside zone 0 may be used in all zones provided that it is supplied by a circuit protected according to Regulation 702.410.3.4.
It is permitted to install an electric heating unit embedded in the floor, provided that it:
(i) is protected by SELV (Section 414). the source of SELV being installed outside zones 0, 1 and 2. However, it is permitted to install the source of SELV in zone 2 if its supply circuit is protected by an RCD having the characteristics specified in Regulation 415.1.1. or
(ii) incorporates an earthed metallic sheath connected to the supplementary equipotential bonding specified in Regulation 702.411.3.3 702.415.2 and its supply circuit is additionally protected by an RCD having the characteristics specified in Regulation 415.1.1. or
(iii) is covered by an embedded earthed metallic grid connected to the supplementary equipotential bonding specified in Regulation 702.411.3.3 702.415.2 and its supply circuit is additionally protected by an RCD having the characteristics specified in Regulation 415.1.1.
(i) Zone 0
This zone is the interior of the basin of the swimming pool or fountain including any recesses in its walls or floors, basins for foot cleaning and water jets or waterfalls and the space below them.
(ii) Zone 1
This zone is limited by:
zone 0
a vertical plane 2 m from the rim of the basin
- the floor or surface expected to be occupied by persons
- the horizontal plane 2.5 m above the floor or the surface expected to be occupied by persons.
Where the swimming pool or fountain contains diving boards, springboards. starting blocks_ chutes or other components expected to be occupied by persons. zone 1 comprises the zone limited by
- a vertical plane situated 1.5 m from the periphery of the diving boards springboards. starting blocks,
chutes and other components such as accessible sculptures_ viewing bays and decorative basins
the horizontal plane 2.5 m above the highest surface expected to be occupied by persons.
(iii) Zone 2
This zone is limited by:
- the vertical plane external to zone 1 and a parallel plane 1 .5 m from the former
- the floor or surface expected to be occupied by persons
- the horizontal plane 2.5 m above the floor or surface expected to be occupied by persons.
There is no zone 2 for fountains.
I will admit I have not read it all. And there is too much to post it all on here so I have just selected those bits which I think are really important.
I think you may not have a TT supply your description sounds like TN but not sure if TN-S or TN-C-S and with the latter as you can see there are special requirements.
One has to be careful with bonding it can make items safer but it can also make items more dangerous and in 2008 the regulations changed and with RCD protection much of the requirements for bonding specially in bathrooms were dropped.
The one which is special is the shaver socket which is an IT supply IT means there is no earth used it's isolated from earth.
If you have TT there will be an earth rod some where it will not get the earth from the oncoming supply.
This is not really a DIY job. You will need test equipment and when mine went in for calibration it cost me £75 to hire a replacement. To buy around £750.
I have always had a copy of BS 7671:2008 to hand so never tried but I would look at the library reference section and see if you can read a copy. Since a member of IET I get mine at special rate but still expensive have not bothered with amendment 1.