Are you sure he was an electrician? Cable does not come as 6A, 16A, 32A, or 40A it comes with a cross sectional area. 1mm², 1.5mm², 2.5mm², 4mm², 6mm² or 10mm² and there are tables to tell you what current it can carry in respect to the installation method.
One looks at the worst installation method over the run of the cable and that becomes the maximum current capacity.
In the main "Reference Method 100# (above a plasterboard ceiling covered by thermal insulation not exceeding 100 mm in thickness)" is the worst but clearly it can vary.
Reference Method 103# (in a stud wall with thermal insulation with cable not touching the inner wall surface) would require a lot thicker cable so for 16A it would require 4mm² cable which with Reference Method C* (Clipped direct) would carry 37A.
As electricians swapping a B32 for a B16 is easy. It's the B16 to B32 which is the problem. If we have the original installation certificate which would state the cable was good for 32A that's easy but without that certificate we need to check the whole route before we could upgrade as without that paperwork we have no idea why it has a B16 MCB.
So some paperwork which states B32 swapped for B16 to comply with manufactures recommendations for oven would be very good in the future when you want a B32 MCB refitted.
But your comments on what the electrician said to me questions if he is really an electrician or a one week wonder retrained under one of the get rich quick retaining schemes?
I am disabled after an industrial accident and have to use tradesmen I would have otherwise never dreamed of using. When my mother had her door bell hard wired it resulted in some words with the installer who was rather surprised to find their client was a member or the IET and had more qualifications than any of their employees.
You could hear the back pacing over the phone as he realised his standard patter would not work.