Extending 30amp Ring Main in Garage From Ring Main
Ask questions and find answers to many subjects relating to electrics and electrical work

4 posts   •   Page 1 of 1
AgedMan
Labourer
Labourer
Posts: 2
Joined: Sat Dec 13, 2014 9:37 am

Extending 30amp Ring Main in Garage From Ring Main

by AgedMan » Sat Dec 13, 2014 10:12 am

I am considering extending the existing 30amp ring main in my garage from an existing ring main socket in the garage (not a spur). Currently the ring main for the upstairs and downstairs are on one 30amp cartridge fuse. The area of the property is approx. 100 m2 including the garage so using the "old" method the ring main should be able to take it. I understand however that the ring main should not be more then 60-70 metres in total length. It is difficult to say the length of the ring main without extension but I would estimate it to be around the 70 metre length in total. All I want to extend the ring main for is to provide a power source for a new roller shutter garage door and put a socket nearer to the tumble dryer rather than using an extension lead for both from the existing ring main socket in the garage which is what I currently do. So ideally I would like to add two double sockets or two single sockets as a minimum. Total additional length 14 lineal metres in total. Any issues here ???

ericmark
Project Manager
Project Manager
Posts: 2870
Joined: Fri Oct 02, 2009 9:49 pm
Location: Llanfair Caereinion, Mid Wales.

Re: Extending 30amp Ring Main in Garage From Ring Main

by ericmark » Sun Dec 14, 2014 12:57 am

Please realise I am now quoting regulations rather than saying what I would do I will get to that after.

1) All new sockets under 30A with the exception of where marked for a single item of equipment i.e. freezer need RCD protection to 30 mA at 40 ms maximum time. It is unlike a fused 30A supply will be RCD protected to 30 mA may be to 100 mA delayed (S type) but not 30 mA.

2) Any buried cable in the wall will also need 30 mA RCD protection if less than 50 mm deep.

3) The loop impedance for a 30A fuse to BS 3036 is 1.09 ohms for a 0.4 s disconnection time. With a B32 MCB it would be 1.44 ohms.

4) The volt drop if wired to BS7671:2001 is 4% if wired to BS7671:2008 i.e. RCD protected then 5%. The volt drop can be calculated from the loop impedance.

5) Under BS7671:2001 or before it was around 80 meters for the volt drop if under BS7671:2008 then 106 meters is the limit. The limit is because of the volt drop and the formula is rather complex. For volt drop we consider with a B32 MCB that the first 20 amp is drawn centre of ring and the remaining 12 amp is even spread so the design current is taken as being 26 amp when working out volt drop.

So in theroy to add extra sockets to a ring designed before 2008 is rather problematic. So now ways around it.

Clearly you have to know what is already there to extend the ring so earth loop impedance meter will be required. If all the extra wires are either special Alu-tube or surface then you could fit RCD sockets however fitting these is expensive.

The other method is to use RCD FCU (fuse connection unit) which will mean you can add many sockets all protected by a single RCD but the total load is only 13A total.

At the consumer unit we fit passive RCD's this means with a power cut they stay connected so with return of power everything still works. But where the loop impedance is too high to ensure there is enough voltage with a short circuit for the device still to work we use an active RCD this means it fails safe and any power cut the RCD will trip and needs resetting. This could be a problem with for example a freezer.

To know if safe to use a passive type you do need to know the loop impedance.

So to use an active RCD FCU and form a spur is reasonably safe when the loop impedance is unknown. But with any other method you need the readings.

The readings should be taken from the centre socket and often a few sockets will need testing to work out which one is centre.

So question is what would happen if to exceed the loop impedance for either the fuse rating or volt drop. Well that 0.4 second figure will be extended. Not too bad with a fuse maybe 0.6 seconds instead of 0.4 seconds but with a MCB it jumps from 0.01 seconds to 1000 seconds if the magic 1.44 ohm is exceeded so extremely important with MCB protection.

As to volt drop well much depends on the equipment. Anything with a switch mode power supply likely unaffected but non electronic fluorescent electric lights will likely fail to light. Radios will have mains hum, and freezers and fridges may burn out the overloads. Battery charger may fail to fully charge a battery.

It is the centre of the ring most affected so it may not be the garage but some other room in the house and if that happens to be the kitchen then fridge/freezer damage is a real problem.

9 times out of 10 extending a ring without testing works OK. But you are taking a risk. As to if electricians test fully I really don't know. But to become a scheme member they have to have the test equipment so one would hope they would use it. They also have to issue a minor works which should show their results.

Because of the price of test equipment near every DIY guy breaks the rules even to hire costs around £75. There are plug in testers with loop test. But every one I have seen the pass lamp comes on at over 1.44 ohms so although the fail lamps shows there is an error the pass lamp does not mean there is no error.

AgedMan
Labourer
Labourer
Posts: 2
Joined: Sat Dec 13, 2014 9:37 am

Re: Extending 30amp Ring Main in Garage From Ring Main

by AgedMan » Sun Dec 14, 2014 3:56 pm

Wow - thank you for your substantive reply. A bit too much information for a DIY question I feel and it sounds in summary that technically a lot of testing should be done as the house and wiring were done in 1982 but balanced by 9 times out of 10 I would be okay to extend the ring main for the purposes identified. Don't really know what to do now. I am sure if I get a qualified electrician to give me a view, he will charge an arm and a leg and may even say more is needed to be done than actually is. What about if I simply took a 13 amp fused spur off the ring main in the garage to serve one single or double socket ?

ericmark
Project Manager
Project Manager
Posts: 2870
Joined: Fri Oct 02, 2009 9:49 pm
Location: Llanfair Caereinion, Mid Wales.

Re: Extending 30amp Ring Main in Garage From Ring Main

by ericmark » Mon Dec 15, 2014 2:29 am

Using a RCD FCU for example the Screwfix SafetySure 13A RCD Fused Spur White Product Code: 26963 is likely the best option you can add as many sockets as you like to that. At £17 not too expensive the double socket SafetySure 13A 2-Gang RCD Unswitched Plug Socket White Product Code: 80534 is same price and nothing to stop you simple plugging in the extras.

I have argued many times with other electricians as to extending a ring and adding a fused spur. For an electrician with all his test gear extending a ring is likely best option but DIY wise then the fused spur is likely best option.

Both the RCD FCU and RCD Socket are passive so will remain energised after a power cut.