by ericmark »
Tue Jan 12, 2016 2:16 am
OK to start with some of the rules we have to follow:-
Any cable needs protecting against overload, in the main we do this at the origin but as long as the cable has no branches and is not more than 3 meters long we can fuse at the destination.
In the main an unfused spur drops into this, although some times more than 3 meters. However it needs to end as a fused connection unit (FCU) or socket with the latter the fuse in the plug is the fuse at the destination.
With fixed appliances they don't need to be supplied with a plug and the manufacturer can stipulate protection required 99% of showers for example say you must use a RCD.
Now traditional cooker connections are 32A and unless the manufacturer says otherwise then supplying an oven or hob or complete cooker from the 32A supply is unlikely to be a problem as long as the cable can take that load so 4 mm sq cable. But with a 45A supply that's not normal and although OK for a cooker or hob in the main a stand alone oven will not take the 6 or 10 mm cable required, however using a duel cooker connection unit and a FCU powering a 3kW or less oven is not really a problem.
However where the oven is over 3kW then it's no longer cut an dried. If we could get a 16A FCU it would be great no idea why not made but without them we can't really connect a 3.8kW oven direct to a 45A fuse or MCB that is going OTT.
There is some debate as to induction hob and power requirement, personally I feel an induction hob uses less power than a halogen hob which is next best so even if rated at 32A it is not going to draw that current for long enough to cause the fuse or trip to open. So to my mind having a duel cooker connection unit and 4mm sq cable to both hob and oven is really no problem with standard size hob.
However with a 45A MCB then it does need either a dedicated 16A supply to oven or a FCU which depends on size of oven.
PS always best to start a new thread, I will often ignore threads already answered until I have loads of free time. Unanswered threads I give priority to.